The simple PLC communication function is available only with the QnUDVCPU and QnUDPVCPU. |
This function allows data
communications between specified devices at the specified timing just by doing simple
settings from a programming tool. Specify one device (transmission source) to one device
(transmission destination). The communications are performed between the specified devices. The communications using this function are not possible when a stop error occurs in the CPU module where the parameters are set. CPU Version
“Simple PLC communicate” by using built-in
Ethernet port, recommend first five digits of S/N is “20042” or later and GX-Works2 version
“1.575z” or later
“Simple PLC communicate” for
iQ-F series by using
built-in Ethernet port, recommend
first five digits of S/N is “20102”
or later and
GX-Works2 version “1.580E” or later
|
|
Setting
Item
|
Description
|
|
READ
|
Read
the data of the specified destination device (transmission source) to the
specified device of the host station (transmission destination).
|
|
WRITE
|
Write the data of the specified device of the host station (transmission source) to the specified destination device (transmission destination). |
|
TRANSFER
|
Read the data of the specified destination device (transmission source) and write it to another specified destination device (transmission destination). |
| Setting Item | Description | Setting range | |
|---|---|---|---|
| Fixed | - | Data are communicated between the devices at a specified execution interval. | - |
| Execution Interval (ms) | Execution interval is set. | 10ms to 65535ms | |
| On Request | - | Data are communicated between the devices only when requested. | - |
| Execution Interval (ms) | Data are communicated at the rising of the device that is specified as Request Contact. | X, M, B | |