How-to use Analog Built in FX5U
How-to use Analog Built in FX5U
How-to use Analog Built in FX5U
Hardware Overview
The Mitsubishi FX5U features various built-in components including:
- Built-in SD Card Slot
- Built-in Analog Input/Output
- Built-in RS-485 Port
- Built-in Ethernet Port
- CPU
- Battery-less and Maintenance-free
- High-speed System Bus Communication (approx. 150-times faster compared with FX3U)
- SSCNET III/H
- CC-Link IE Field
| Item |
Specifications |
| No. of analog input points |
2 points (2 channels) |
| Analog input (Voltage) |
0 to 10 V DC (input resistance 115.7 kΩ) |
| Digital output |
Unsigned 12-bit binary |
| Device allocation |
SD6020 (Input data of ch1), SD6060 (Input data of ch2) |
| Max. resolution |
2.5 mV (Digital output value 0 to 4000) |
| Precision (25 ±5°C) |
Within ±0.5 % (±20 digit) |
| Conversion speed |
30 μs /Channel (data refreshed every operation cycle) |
| Absolute max. input |
-0.5 V, +15 V |
| Insulation method |
Not insulated inside CPU module or between channels |
*1 Specification applies to products manufactured from June 2016.
*2 "Digit" refers to digital values.
| List of Functions |
Description |
| A/D conversion enable/disable setting |
Enable or disable conversion per channel to reduce process time. |
| A/D conversion method |
Includes Sampling processing, Time average, Count average, and Moving average. |
| Over scale detection function |
Detects analog input values exceeding the range. |
| Scaling function |
Converts digital values according to a configured scale. |
| Shift function |
Adds a specified amount to the A/D conversion value for fine adjustments. |
| Digital clipping function |
Clips values to maximum (4000) or minimum (0) when range is exceeded. |
| Warning output function |
Outputs warning when digital operation values exceed specified range. |
| Event history function |
Stores errors and events into the CPU module. |
Terminal Layout
| Signal Name |
Terminal |
Function |
| Analog input |
V1+ |
CH1 Voltage input (+) |
| V2+ |
CH1 Voltage input (+) |
| V- |
CH1/CH2 Voltage input (-) |
| Analog output |
V+ |
CH1 Voltage output (+) |
| V- |
CH1 Voltage output (-) |
Wiring Notes
- Use shielded twisted-pair cables (double-core type).
- Separate cables from power lines or lines with induction.
- Short-circuit "V+" and "V-" terminals for unused channels.
- Use Class D grounding.
| Description |
CH1 |
CH2 |
R/W |
| A/D conversion completed flag |
SM6020 |
SM6060 |
R |
| A/D conversion enable/disable setting |
SM6021 |
SM6061 |
R/W |
| Warning output flag (upper limit) |
SM6031 |
SM6071 |
R |
| Warning output flag (lower limit) |
SM6032 |
SM6072 |
R |
| A/D conversion error flag |
SM6059 |
SM6099 |
R |
| Description |
CH1 |
CH2 |
R/W |
| Digital output value |
SD6020 |
SD6060 |
R |
| Digital operation value |
SD6021 |
SD6061 |
R |
| Scaling upper limit value |
SD6028 |
SD6068 |
R/W |
| Scaling lower limit value |
SD6029 |
SD6069 |
R/W |
| Process alarm upper upper limit value |
SD6031 |
SD6071 |
R/W |
Setting Procedure
- Access Parameter settings and select "Analog Input".
- Enable CH1. Data can be read from register SD6020.
- Choose from 4 Average functions: Sampling, Time, Count, or Moving Average.
Warning Output Setting
Enable the Warning Output Function to receive alerts via SM6031 and SM6032.
- Example: Set Upper Limit to 3000 (Alert via SM6031).
- Example: Set Lower Limit to 500 (Alert via SM6032).
Scaling Setting
Use the Scaling Setting function to define the range of incoming values. Values will be reflected in SD6021 (e.g., 0-3000).
Analog Output Specifications
| Item |
Specifications |
| No. of analog output points |
1 point (1 channel) |
| Digital input |
Unsigned 12-bit binary |
| Analog output (Voltage) |
0 to 10 V DC (load 2 k to 1 MΩ) |
| Device allocation |
SD6180 (Output setting data) |
| Max. resolution |
2.5 mV (Digital input 0 to 4000) |
| Precision (25 ±5°C) |
Within ±0.5 % (±20 digit) |
| Conversion speed |
30 μs (refreshed every cycle) |
Analog Output Functions
| List of Functions |
Description |
| D/A conversion enable/disable |
Enables or disables conversion. |
| Analog output HOLD/CLEAR |
Sets output to previous value or 0 during CPU STOP or error. |
| Scaling function |
Converts user-defined max/min digital values to scale. |
| Warning output function |
Checks digital values against upper/lower limits. |
Wiring Notes
- Use shielded twisted-pair cables.
- Ground the shielded cable at one point on the signal receiving side.pecial Devices for Analog Output
| Description |
Special Relay |
Special Register |
R/W |
| D/A conversion enable/disable |
SM6180 |
- |
R/W |
| Digital value (Output setting) |
- |
SD6180 |
R/W |
| Digital operation value |
- |
SD6181 |
R |
| Warning output upper limit flag |
SM6191 |
- |
R |
| Warning output lower limit flag |
SM6192 |
- |
R |
Analog Output Setting
- Access Parameter settings and select "Analog Output".
- Enable the channel. Output data is sent via SD6180.
- Important: Both "Conversion" and "Output" must be enabled.
Application Examples
- Warning: Set SM6191 to trigger if output exceeds 3000, and SM6192 if below 100.
- Scaling: Define a range (e.g., 0-3000) for SD6180.
- Example: Writing 3000 to SD6180 (with scaling 0-3000) will result in a 10V output.
Related Articles
SIMPLE PLC COMMUNICATION FUNCTION For Q Series [Built-in Ethernet port]
SIMPLE PLC COMMUNICATION FUNCTION The simple PLC communication function is available only with the QnUDVCPU and QnUDPVCPU. This function allows data communications between specified devices at the specified timing just by doing simple settings from a ...
SIMPLE PLC COMMUNICATION FUNCTION For iQ-F Series [FX5U, FX5UJ, FX5UC]
SIMPLE PLC COMMUNICATION FUNCTION FX5U/FX5UC CPU module is supported. (Firmware version "1.210" and above) This function allows data communications between specified devices at the specified timing just by doing simple settings from a programming ...
4 things you should know before choosing the right PLC for your application.
01. What voltage does it use? Electrical usage is a crucial aspect, directly related to user and operator safety. PLCs accept two types of power sources: ● AC (e.g., 100-240V) ● DC (e.g., 24V) Another important aspect is the input/output current. The ...
iQ-R basic settings
iQ-R Configuration 1. Press “Module Configuration” 2. Press “Element Selection” then choose components 3. AFTER CLOSE, IT WILL AUTO SHOW 0000 AND 0010 AT MODULE INFORMATION iQ-R Analog Settings 1. WIRING MODULE R60DAI8 2. SETTING 3. LADDER
iQ-F basic settings
iQ-F Configuration 1. Press “Module Configuration” 2. Press “Element Selection” 3. Choose ”FX5-4DA-ADP” 4. DRAG AND MOVE 5. AFTER CLOSE, ICON ADP1 WILL SHOW AT MODULE INFORMATION. iQ-F Analog Settings 1. WIRING MODULE FX5-4DA-ADP 2. SETTING 3. LADDER