How-to use Analog Built in FX5U

How-to use Analog Built in FX5U

How-to use Analog Built in FX5U

How-to use Analog Built in FX5U

Hardware Overview

The Mitsubishi FX5U features various built-in components including:

  • Built-in SD Card Slot
  • Built-in Analog Input/Output
  • Built-in RS-485 Port
  • Built-in Ethernet Port
  • CPU
  • Battery-less and Maintenance-free
  • High-speed System Bus Communication (approx. 150-times faster compared with FX3U)
  • SSCNET III/H
  • CC-Link IE Field

Analog Input Specifications

Item Specifications
No. of analog input points 2 points (2 channels)
Analog input (Voltage) 0 to 10 V DC (input resistance 115.7 kΩ)
Digital output Unsigned 12-bit binary
Device allocation SD6020 (Input data of ch1), SD6060 (Input data of ch2)
Max. resolution 2.5 mV (Digital output value 0 to 4000)
Precision (25 ±5°C) Within ±0.5 % (±20 digit)
Conversion speed 30 μs /Channel (data refreshed every operation cycle)
Absolute max. input -0.5 V, +15 V
Insulation method Not insulated inside CPU module or between channels

*1 Specification applies to products manufactured from June 2016.

*2 "Digit" refers to digital values.




List of Functions Description
A/D conversion enable/disable setting Enable or disable conversion per channel to reduce process time.
A/D conversion method Includes Sampling processing, Time average, Count average, and Moving average.
Over scale detection function Detects analog input values exceeding the range.
Scaling function Converts digital values according to a configured scale.
Shift function Adds a specified amount to the A/D conversion value for fine adjustments.
Digital clipping function Clips values to maximum (4000) or minimum (0) when range is exceeded.
Warning output function Outputs warning when digital operation values exceed specified range.
Event history function Stores errors and events into the CPU module.

Terminal Layout

Signal Name Terminal Function
Analog input V1+ CH1 Voltage input (+)
V2+ CH1 Voltage input (+)
V- CH1/CH2 Voltage input (-)
Analog output V+ CH1 Voltage output (+)
V- CH1 Voltage output (-)

Wiring Notes

  • Use shielded twisted-pair cables (double-core type).
  • Separate cables from power lines or lines with induction.
  • Short-circuit "V+" and "V-" terminals for unused channels.
  • Use Class D grounding.

Special Relays for Analog Input

Description CH1 CH2 R/W
A/D conversion completed flag SM6020 SM6060 R
A/D conversion enable/disable setting SM6021 SM6061 R/W
Warning output flag (upper limit) SM6031 SM6071 R
Warning output flag (lower limit) SM6032 SM6072 R
A/D conversion error flag SM6059 SM6099 R

Special Registers for Analog Input

Description CH1 CH2 R/W
Digital output value SD6020 SD6060 R
Digital operation value SD6021 SD6061 R
Scaling upper limit value SD6028 SD6068 R/W
Scaling lower limit value SD6029 SD6069 R/W
Process alarm upper upper limit value SD6031 SD6071 R/W

Setting Procedure

  1. Access Parameter settings and select "Analog Input".
  2. Enable CH1. Data can be read from register SD6020.
  3. Choose from 4 Average functions: Sampling, Time, Count, or Moving Average.

Warning Output Setting

Enable the Warning Output Function to receive alerts via SM6031 and SM6032.

  • Example: Set Upper Limit to 3000 (Alert via SM6031).
  • Example: Set Lower Limit to 500 (Alert via SM6032).

Scaling Setting

Use the Scaling Setting function to define the range of incoming values. Values will be reflected in SD6021 (e.g., 0-3000).


Analog Output Specifications

Item Specifications
No. of analog output points 1 point (1 channel)
Digital input Unsigned 12-bit binary
Analog output (Voltage) 0 to 10 V DC (load 2 k to 1 MΩ)
Device allocation SD6180 (Output setting data)
Max. resolution 2.5 mV (Digital input 0 to 4000)
Precision (25 ±5°C) Within ±0.5 % (±20 digit)
Conversion speed 30 μs (refreshed every cycle)

Analog Output Functions

List of Functions Description
D/A conversion enable/disable Enables or disables conversion.
Analog output HOLD/CLEAR Sets output to previous value or 0 during CPU STOP or error.
Scaling function Converts user-defined max/min digital values to scale.
Warning output function Checks digital values against upper/lower limits.

Wiring Notes

  • Use shielded twisted-pair cables.
  • Ground the shielded cable at one point on the signal receiving side.pecial Devices for Analog Output
Description Special Relay Special Register R/W
D/A conversion enable/disable SM6180 - R/W
Digital value (Output setting) - SD6180 R/W
Digital operation value - SD6181 R
Warning output upper limit flag SM6191 - R
Warning output lower limit flag SM6192 - R


Analog Output Setting

  1. Access Parameter settings and select "Analog Output".
  2. Enable the channel. Output data is sent via SD6180.
  3. Important: Both "Conversion" and "Output" must be enabled.

Application Examples

  • Warning: Set SM6191 to trigger if output exceeds 3000, and SM6192 if below 100.
  • Scaling: Define a range (e.g., 0-3000) for SD6180.
  • Example: Writing 3000 to SD6180 (with scaling 0-3000) will result in a 10V output.

    • Related Articles

    • SIMPLE PLC COMMUNICATION FUNCTION For Q Series [Built-in Ethernet port]

      SIMPLE PLC COMMUNICATION FUNCTION The simple PLC communication function is available only with the QnUDVCPU and QnUDPVCPU. This function allows data communications between specified devices at the specified timing just by doing simple settings from a ...
    • iQ-F, iQ-R basic settings

      iQ-F Configuration 1. Press “Module Configuration” 2. Press “Element Selection” 3. Choose ”FX5-4DA-ADP” 4. DRAG AND MOVE 5. AFTER CLOSE, ICON ADP1 WILL SHOW AT MODULE INFORMATION. iQ-F Analog Settings 1. WIRING MODULE FX5-4DA-ADP 2. SETTING 3. LADDER ...